Ventilation Requirements
Do not block the air vents on the XR8 terminal. A minimum of 100 mm (4 inches) of clearance must be provided on the sides where air vents are located (left, right, and rear). This is required for proper cooling of the unit.
If unit is installed in a customer enclosure
The following guidelines must be observed when placing the terminal inside an enclosure:
•Ventilation clearance requirements noted above must always be followed.
•If terminal is completely enclosed (six-sided) front doors and rear of enclosure must allow adequate airflow (be vented) through the enclosure from front to back.
•In a five-sided enclosure (no doors on the front) a few inches clearance on top of the unit is also required if the rear of the enclosure is not properly vented.
•Venting must be to the degree that the enclosure will maintain an internal temperature as close to room ambient temperature as possible, and always below the maximum specified operating temperature (40°C / 104°F).
Note: Cabinet/Enclosure modifications may be required at the customer location to accommodate these site preparation requirements.